I'm mostly a lurker, and don't even got to the space with any kind of
regularity, so feel free to disregard what I have to say.

However, I am a state licensed electrician.

It's a bad idea to put all the lights on one phase (which is hopefully
what all the red wires are) and all the plugs on a different phase.

Two reasons come to mind. One: if there should ever be a power outage
on one phase, you might lose all the lights. (Though this is unlikely)
Two: someone might want power for a 220v machine some time. You need
separate phases for that, and you should NEVER run separate phases
with the same color wire. IMHO, that's how someone will die/start a
fire/do other bad things.

That's just my two cents though, Neil and Tim probably also have input.

On Fri, May 2, 2014 at 10:10 PM, Naomi Most <pnaomi at gmail.com> wrote:
> Jim's own list of identified problems with NB's electrical infrastructure.
>
> I'm guessing there is some overlap with what you guys took down, Neil and Tim.
>
>
>
> ---------- Forwarded message ----------
> From: jim <jim at well.com>
> Date: Fri, May 2, 2014 at 12:25 PM
> Subject: Re: [Noisebridge-discuss] The electricians are coming! (today
> between 4 and 5pm)
> To: maestro <maestro415 at gmail.com>
> Cc: Noisebridge-discuss <Noisebridge-discuss at lists.noisebridge.net>
>
>
>
> (thank you, Maestro)
>
> To whoever is in charge,
>
> Please forward the short list of eggrecences below
> to the electricians; it specifies some things that
> they may initially miss:
>
> South wall west : 1/2" pipe from sub-panel and
> perhaps four square boxes need proper straps
> and anchors.
>
> West wall center : receptacle boxes and pipe
> feeding them need proper straps and anchors.
>
> North wall west : sub-panel fed from floor
> internal bus should be screwed tight; cover
> needs proper screws; one of the multiple breakers
> has a broken breaker (I recall it's the 100 A
> breaker that controls the kitchen sub-panel).
>
> North wall Turing, center of room, floor : junction
> box is open; there is a red, white, and black
> (supplied by the sub-panel at the top of the
> stairwell) that can be used for the Church
> classroom--that will need a 1/2" pipe from the
> floor box to a new junction box in the Church
> classroom: pair red and black with a single white,
> use red for lights and black for receptacles.
>
> Kitchen sub-panel (supplied by 100A three-pole
> breaker in the north-west sub-panel) : the kitchen
> sub-panel is a mess inside; pipes coming out of it
> to the south wall of the sinks should be properly
> offset or supported as well as properly strapped
> and anchored.
>
> Generally okay (as I recall):
> * most of the Turing wall and ceiling work
> * most of the DJ booth work
> * work for both toilet rooms
> * all of the darkroom
> * most of the pipes on the ceiling
> * most of the work in the dirty shop
> I.e. no hidden problems.
>
>
>
> On 05/02/2014 12:05 PM, maestro wrote:
>
> A perfect example of an EXCELLENT person NB has lost due to all the
> bullshit @ the house.
>
> Thank you jim for all your work to the space electrically, the money
> you have put into it in multiple ways, teaching, and sharing in
> attempts to foster positive DO-ocracy and a positive freely creative
> environment...
>
> Message ends
> ________________
>
>
>
>
> On Friday, May 2, 2014, jim <jim at well.com> wrote:
>>
>>     I did some (not all) of the work to adjust
>> from the previous tenant's needs to Noisebridge's
>> needs.
>>     Because the space is a hacker space, it
>> seemed (and seems) to me that there should
>> be particular consistency in the wiring, given
>> that hackers have the courage to get into
>> stuff they don't understand until after they
>> have gotten in:
>> * black wires are used to power receptacles
>> * red wires are used to power lights and
>>   appliances
>> * blue wires indicate the "third leg" of the
>>   three phase sub-panels.
>>
>>     The idea is that hackers may trip breakers
>> from time to time. Especially at night, it's a
>> bad idea that lights go out if a breaker trips--
>> a matter of safety.
>>     Please convey this idea to the electricians.
>> Note that in some circumstances, the
>> electrical code specifies that lights not share
>> breakers with receptacles. What I tried to do
>> was to extend this principle to the entire space
>> (again, as a matter of safety).
>>
>>
>>
>> On 05/02/2014 12:20 AM, Naomi Most wrote:
>>>
>>> Hi everybody,
>>>
>>> Electricians Neil and Tim came by earlier.  They were quite thorough,
>>> took pictures and notes, and asked a lot of questions about usage.
>>>
>>> They seemed to feel there weren't any major scary things wrong, but
>>> there were many minor nicks and cuts that we should probably patch up.
>>>
>>> They're going to make up a list of "red flag" and "yellow flag" items
>>> and give us rough estimates for costs to fix.  They know we'll want to
>>> fix lots of things ourselves, too, so they're keeping that in mind.
>>>
>>> I also wrote down a list of electrical to-do items based on their
>>> observations that we can definitely do ourselves.  I'll post that
>>> tomorrow.
>>>
>>> Finally, a bunch of folks would like to start coordinating on physical
>>> space maintenance and improvements on a separate mailing list.  I
>>> propose using Build:
>>>
>>> https://www.noisebridge.net/mailman/listinfo/build
>>>
>>> Cheers,
>>> Naomi
>>>
>>> On Thu, May 1, 2014 at 2:31 PM, Henner Zeller <h.zeller at acm.org> wrote:
>>>>
>>>> On 1 May 2014 14:22, Naomi Most <pnaomi at gmail.com> wrote:
>>>>>
>>>>> There are two C-10 certified electricians coming to Noisebridge in a few hours.
>>>>>
>>>>> I'll be there to walk through the space and note their comments.  I'll
>>>>> report back to this list on their findings.
>>>>
>>>> Thanks for getting this sorted and investing your time walking them through.
>>>>
>>>> H.
>>>>
>>>>> Don't worry: today there is no money being spent or committed to be
>>>>> spent.  This is a free consultation to help us decide how to address
>>>>> the city's concerns about our safety.
>>>>>
>>>>> Cheers,
>>>>> Naomi
>>>>>
>>>>>
>>>>> --
>>>>> Naomi Theora Most
>>>>> naomi at nthmost.com
>>>>> +1-415-728-7490
>>>>>
>>>>> skype: nthmost
>>>>>
>>>>> http://twitter.com/nthmost
>>>>> _______________________________________________
>>>>> Noisebridge-discuss mailing list
>>>>> Noisebridge-discuss at lists.noisebridge.net
>>>>> https://www.noisebridge.net/mailman/listinfo/noisebridge-discuss
>>>
>>>
>>
>> _______________________________________________
>> Noisebridge-discuss mailing list
>> Noisebridge-discuss at lists.noisebridge.net
>> https://www.noisebridge.net/mailman/listinfo/noisebridge-discuss
>>
>
> --
>
> ~the quieter you become, the more you are able to hear...
>
>
>
>
> _______________________________________________
> Noisebridge-discuss mailing list
> Noisebridge-discuss at lists.noisebridge.net
> https://www.noisebridge.net/mailman/listinfo/noisebridge-discuss
>
>
>
> --
> Naomi Theora Most
> naomi at nthmost.com
> +1-415-728-7490
>
> skype: nthmost
>
> http://twitter.com/nthmost
> _______________________________________________
> Build mailing list
> Build at lists.noisebridge.net
> https://www.noisebridge.net/mailman/listinfo/build



More information about the Build mailing list